Hot questions in Power Systems
0
votes
0
answers
41
GATE Electrical 2014 Set 1 | Question: 40
A distribution feeder of $1\:km$ length having resistance, but negligible reactance, is fed from both the ends by $400V$, $50\:Hz$ balanced sources. Both voltage sources $S_1$ and $S_2$ are in phase. The feeder supplies concentrated loads of unity power factor as shown in the figure. ... $25\:A$ $50\:A$ and $50\:A$ $25\:A$ and $75\:A$ $0\:A$ and $100\:A$
A distribution feeder of $1\:km$ length having resistance, but negligible reactance, is fed from both the ends by $400V$, $50\:Hz$ balanced sources. Both voltage sources ...
makhdoom ghaya
9.4k
points
makhdoom ghaya
asked
Feb 11, 2017
Power Systems
gate2014-ee-1
single-line-diagram
distribution
feeder
+
–
0
votes
0
answers
42
GATE Electrical 2015 Set 1 | Question: 54
Find the transfer function $\dfrac{Y(s)}{X(s)}$ of the system given below $\dfrac{G_{1}}{1-HG_{1}} + \dfrac{G_{2}}{1-HG_{2}} \\$ $\dfrac{G_{1}}{1+HG_{1}} + \dfrac{G_{2}}{1+HG_{2}} \\$ $\dfrac{G_{1}+G_{2}}{1+H (G_{1}+G_{2})} \\$ $\dfrac{G_{1}+G_{2}}{1-H (G_{1}+G_{2})}$
Find the transfer function $\dfrac{Y(s)}{X(s)}$ of the system given below$\dfrac{G_{1}}{1-HG_{1}} + \dfrac{G_{2}}{1-HG_{2}} \\$$\dfrac{G_{1}}{1+HG_{1}} + \dfrac{G_{2}}{1+...
makhdoom ghaya
9.4k
points
makhdoom ghaya
asked
Feb 11, 2017
Power Systems
gate2015-ee-1
power-systems
transfer-function
feedback-system
+
–
0
votes
0
answers
43
GATE Electrical 2014 Set 2 | Question: 41
There are two generators in a power system. No-load frequencies of the generators are $51.5$ $Hz$ and $51$ $Hz$, respectively, and both are having droop constant of $1$ $Hz$/$MW$. Total load in the system is ... are operating under their respective droop characteristics, the frequency of the power system in $Hz$ in the steady state is ___________.
There are two generators in a power system. No-load frequencies of the generators are $51.5$ $Hz$ and $51$ $Hz$, respectively, and both are having droop constant of $1$ $...
makhdoom ghaya
9.4k
points
makhdoom ghaya
asked
Feb 11, 2017
Power Systems
gate2014-ee-2
power-system-analysis
power-production
numerical-answers
+
–
0
votes
0
answers
44
GATE Electrical 2014 Set 3 | Question: 42
The complex power consumed by a constant-voltage load is given by $(P_1+jQ_1)$, where, $1 \: kW \leq P_1 \leq 1.5 \text{ kW}$ and $0.5 \: \text{kVAR} \leq Q_1 \leq 1 \text{ kVAR}$. A compensating shunt ... is the net reactive power consumed by the capacitor-load combination. The reactive power (in $\text{kVAR}$) supplied by the capacitor is _________.
The complex power consumed by a constant-voltage load is given by $(P_1+jQ_1)$, where, $1 \: kW \leq P_1 \leq 1.5 \text{ kW}$ and $0.5 \: \text{kVAR} \leq Q_1 \leq 1 \te...
makhdoom ghaya
9.4k
points
makhdoom ghaya
asked
Feb 11, 2017
Power Systems
gate2014-ee-3
capacitor-load-combination
numerical-answers
+
–
0
votes
0
answers
45
GATE Electrical 2015 Set 1 | Question: 51
Two single-phase transformers $T_{1}$ and $T_{2}$ each rated at $500$ kVA are operated in parallel. Percentage impedances of $T_{1}$ and $T_{2}$ are $(1 + j6)$ and $(0.8 + j4.8)$, respectively. To share a load of $1000$ kVA at $0.8$ lagging power factor, the contribution of $T_{2}$ (in kVA) is _______.
Two single-phase transformers $T_{1}$ and $T_{2}$ each rated at $500$ kVA are operated in parallel. Percentage impedances of $T_{1}$ and $T_{2}$ are $(1 + j6)$ and $(0.8 ...
makhdoom ghaya
9.4k
points
makhdoom ghaya
asked
Feb 11, 2017
Power Systems
gate2015-ee-1
lagging-power-factor
single-phase-transformers
numerical-answers
+
–
0
votes
0
answers
46
GATE Electrical 2014 Set 2 | Question: 47
Suppose that resistors $R_1$ and $R_2$ are connected in parallel to give an equivalent resistor $R$. If resistors $R_1$ and $R_2$ have tolerance of $1 \%$ each, the equivalent resistor $R$ for resistors $R_1=300\: \Omega$ and $R_2 = 200 \: \Omega$ will have tolerance of $0.5 \%$ $1 \%$ $1.2 \%$ $2 \%$
Suppose that resistors $R_1$ and $R_2$ are connected in parallel to give an equivalent resistor $R$. If resistors $R_1$ and $R_2$ have tolerance of $1 \%$ each, the equiv...
makhdoom ghaya
9.4k
points
makhdoom ghaya
asked
Feb 11, 2017
Power Systems
gate2014-ee-2
power-systems
parallel-combination
tolerance
+
–
0
votes
0
answers
47
GATE Electrical 2013 | Question: 45
A $4$ – pole induction motor, supplied by a slightly unbalanced three-phase $50 Hz$ source, is rotating at $1400\:rpm$. The electrical frequency in $Hz$ of the induced negative sequence current in the rotor is $100$ $98$ $52$ $48$
A $4$ – pole induction motor, supplied by a slightly unbalanced three-phase $50 Hz$ source, is rotating at $1400\:rpm$. The electrical frequency in $Hz$ of the induced ...
piyag476
1.6k
points
piyag476
asked
Feb 11, 2017
Power Systems
gate2013-ee
salient-poles
sequence-current
+
–
0
votes
0
answers
48
GATE Electrical 2015 Set 1 | Question: 43
A $50 \text{ Hz}$ generating unit has H-constant of $2 \text{ MJ/MVA}$. The machine is initially operating in steady state at synchronous speed, and producing $1 \:pu$ of real power. The initial value of the rotor angle $\delta$ ... power to remain at $1 \: pu$, the value of $\delta$ in degrees, $0.02$ second after the fault is _________.
A $50 \text{ Hz}$ generating unit has H-constant of $2 \text{ MJ/MVA}$. The machine is initially operating in steady state at synchronous speed, and producing $1 \:pu$ of...
makhdoom ghaya
9.4k
points
makhdoom ghaya
asked
Feb 11, 2017
Power Systems
gate2015-ee-1
short-circuit-fault
synchronous-speed
numerical-answers
+
–
0
votes
0
answers
49
GATE Electrical 2013 | Question: 47
When the $\text{Newton-Raphson}$ method is applied to solve the equation $f(x)=x^3+2x-1=0$ ,the solution at the end of the first iteration with the initial guess value as $x_0$ =$1.2$ is $-0.82$ $0.49$ $0.705$ $1.69$
When the $\text{Newton-Raphson}$ method is applied to solve the equation $f(x)=x^3+2x-1=0$ ,the solution at the end of the first iteration with the initial guess value a...
piyag476
1.6k
points
piyag476
asked
Feb 11, 2017
Power Systems
gate2013-ee
iterative-techniques
line-losses
+
–
0
votes
0
answers
50
GATE Electrical 2014 Set 2 | Question: 12
A single phase, $50$ $kVA$, $1000V$/$100V$ two winding transformer is connected as an autotransformer as shown in the figure. The $kVA$ rating of the autotransformer is _____________.
A single phase, $50$ $kVA$, $1000V$/$100V$ two winding transformer is connected as an autotransformer as shown in the figure.The $kVA$ rating of the autotransformer is __...
makhdoom ghaya
9.4k
points
makhdoom ghaya
asked
Feb 11, 2017
Power Systems
gate2014-ee-2
auto-transformer
step-down-transformer
numerical-answers
+
–
0
votes
0
answers
51
GATE Electrical 2014 Set 2 | Question: 15
A three phase star-connected load is drawing power at a voltage of $0.9$ $pu$ and $0.8$ power factor lagging. The three phase base power and base current are $100$ $MVA$ and $437.384$ $A$ respectively. The line-to-line load voltage in $kV$ is ________.
A three phase star-connected load is drawing power at a voltage of $0.9$ $pu$ and $0.8$ power factor lagging. The three phase base power and base current are $100$ $MVA$ ...
makhdoom ghaya
9.4k
points
makhdoom ghaya
asked
Feb 11, 2017
Power Systems
gate2014-ee-2
power-factor
star-connection
numerical-answers
+
–
0
votes
0
answers
52
GATE Electrical 2015 Set 1 | Question: 12
A steady current $I$ is flowing in the $-x$ direction through each of two infinitely long wires at $y = \pm \dfrac{L}{2}$ as shown in the figure. The permeability of the medium is $\mu_{0}$. The $\overrightarrow{B}$-field at $(0,L,0)$ ... $+\dfrac{4\mu _{0}I}{3\Pi L} \hat{Z} \\$ $0 \\$ $-\dfrac{3\mu _{0}I}{4\Pi L} \hat{Z}$
A steady current $I$ is flowing in the $-x$ direction through each of two infinitely long wires at $y = \pm \dfrac{L}{2}$ as shown in the figure. The permeability of the ...
makhdoom ghaya
9.4k
points
makhdoom ghaya
asked
Feb 11, 2017
Power Systems
gate2015-ee-1
permeability
steady-current
+
–
0
votes
0
answers
53
GATE Electrical 2016 Set 2 | Question: 53
Two identical unloaded generators are connected in parallel as shown in the figure. Both the generators are having positive, negative and zero sequence impedances of $j0.4$ p.u., $j0.3$ p.u. and $j0.15$ p.u., respectively. If the pre-fault ... a line-to-ground $(L-G)$ fault at the terminals of the generators, the fault current, in p.u., is ___________.
Two identical unloaded generators are connected in parallel as shown in the figure. Both the generators are having positive, negative and zero sequence impedances of $j0....
makhdoom ghaya
9.4k
points
makhdoom ghaya
asked
Jan 29, 2017
Power Systems
gate2016-ee-2
sequence-impedences
pre-fault-voltage
numerical-answers
+
–
0
votes
0
answers
54
GATE Electrical 2016 Set 2 | Question: 36
In the balanced $3$-phase, $50$ Hz, circuit shown below, the value of inductance $(L)$ is $10$ mH. The value of the capacitance $(C)$ for which all the line currents are zero, in millifarads, is ___________.
In the balanced $3$-phase, $50$ Hz, circuit shown below, the value of inductance $(L)$ is $10$ mH. The value of the capacitance $(C)$ for which all the line currents are ...
makhdoom ghaya
9.4k
points
makhdoom ghaya
asked
Jan 29, 2017
Power Systems
gate2016-ee-2
balanced-system
line
currents
numerical-answers
+
–
0
votes
0
answers
55
GATE Electrical 2016 Set 1 | Question: 21
Consider a system consisting of a synchronous generator working at a lagging power factor, a synchronous motor working at an overexcited condition and a directly grid-connected induction generator. Consider capacitive $VAr$ to be a ... source and induction generator and synchronous generator are sinks of reactive power. All are sources of reactive power.
Consider a system consisting of a synchronous generator working at a lagging power factor, a synchronous motor working at an overexcited condition and a directly grid-con...
makhdoom ghaya
9.4k
points
makhdoom ghaya
asked
Jan 29, 2017
Power Systems
gate2016-ee-1
unity-power-factor
source-of-reactive-power
load
+
–
1
votes
0
answers
56
GATE Electrical 2016 Set 2 | Question: 38
The single line diagram of a balanced power system is shown in the figure. The voltage magnitude at the generator internal bus is constant and $1.0$ p.u. The p.u. reactances of different components in the system are ... transferred during the pre-fault condition to the maximum real power that can be transferred under the faulted condition is _________.
The single line diagram of a balanced power system is shown in the figure. The voltage magnitude at the generator internal bus is constant and $1.0$ p.u. The p.u. reactan...
makhdoom ghaya
9.4k
points
makhdoom ghaya
asked
Jan 29, 2017
Power Systems
gate2016-ee-2
single-line-diagram
three-phase-fault
pre-fault-condition
numerical-answers
+
–
0
votes
0
answers
57
GATE Electrical 2016 Set 2 | Question: 13
A power system with two generators is shown in the figure below. The system (generators, buses and transmission lines) is protected by six overcurrent relays $R_{1}$ to $R_{6}$ ... are $R_{1}, R_{2}$ $R_{2}, R_{6}$ $R_{2}, R_{5}$ $R_{1}, R_{6}$
A power system with two generators is shown in the figure below. The system (generators, buses and transmission lines) is protected by six overcurrent relays $R_{1}$ to $...
makhdoom ghaya
9.4k
points
makhdoom ghaya
asked
Jan 29, 2017
Power Systems
gate2016-ee-2
power-system-protection
magnitude-comparison-relays
zone-of-protection
pick-up-current
+
–
0
votes
0
answers
58
GATE Electrical 2016 Set 2 | Question: 51
Three single-phase transformers are connected to form a delta-star three-phase transformer of $110$ kV/ $11$ kV. The transformer supplies at $11$ kV a load of $8$ MW at $0.8$ p.f. lagging to a nearby plant. Neglect the transformer losses. The ratio of phase currents in delta side to star side is $1 : 10\sqrt{3}$ $10\sqrt{3} : 1$ $1 : 10$ $\sqrt{3} : 10$
Three single-phase transformers are connected to form a delta-star three-phase transformer of $110$ kV/ $11$ kV. The transformer supplies at $11$ kV a load of $8$ MW at $...
makhdoom ghaya
9.4k
points
makhdoom ghaya
asked
Jan 29, 2017
Power Systems
gate2016-ee-2
delta-star-connections
transformer-losses
+
–
0
votes
0
answers
59
GATE Electrical 2016 Set 2 | Question: 41
The power consumption of an industry is $500$ kVA, at $0.8$ p.f. lagging. A synchronous motor is added to raise the power factor of the industry to unity. If the power intake of the motor is $100$ kW, the p.f. of the motor is ___________.
The power consumption of an industry is $500$ kVA, at $0.8$ p.f. lagging. A synchronous motor is added to raise the power factor of the industry to unity. If the power in...
makhdoom ghaya
9.4k
points
makhdoom ghaya
asked
Jan 29, 2017
Power Systems
gate2016-ee-2
synchronous-motor
power-factor
power-intake
numerical-answers
+
–
0
votes
0
answers
60
GATE Electrical 2016 Set 1 | Question: 20
The magnitude of three-phase fault currents at buses $A$ and $B$ of a power system are $10$ pu and $8$ pu, respectively. Neglect all resistances in the system and consider the pre-fault system to be unloaded. The pre-fault voltage at all buses in the ... $0.8$ pu. The voltage magnitude at bus $A$ during a three-phase fault at bus $B$, in pu, is __________.
The magnitude of three-phase fault currents at buses $A$ and $B$ of a power system are $10$ pu and $8$ pu, respectively. Neglect all resistances in the system and conside...
makhdoom ghaya
9.4k
points
makhdoom ghaya
asked
Jan 29, 2017
Power Systems
gate2016-ee-1
fault-analysis
power-system-buses
3-phase-short-circuit
numerical-answers
+
–
0
votes
0
answers
61
GATE Electrical 2016 Set 2 | Question: 35
The $z$-parameters of the two port network shown in the figure are $z_{11}=40\Omega, z_{12}=60\Omega, z_{21}=80\Omega$ and $z_{22}=100\Omega$. The average power delivered to $R_{L}=20\Omega$, in watts, is ________.
The $z$-parameters of the two port network shown in the figure are $z_{11}=40\Omega, z_{12}=60\Omega, z_{21}=80\Omega$ and $z_{22}=100\Omega$. The average power delivered...
makhdoom ghaya
9.4k
points
makhdoom ghaya
asked
Jan 29, 2017
Power Systems
gate2016-ee-2
average-power
network-analysis
numerical-answers
+
–
0
votes
0
answers
62
GATE Electrical 2016 Set 2 | Question: 15
The inductance and capacitance of a $400$ kV, three-phase, $50$ Hz lossless transmission line are $1.6$ mH/km/phase and $10$ nF/km/phase respectively. The sending end voltage is maintained at $400$ kV. To maintain a ... at the receiving end, when the line is delivering $300$ MW load, the shunt compensation required is Capacitive Inductive Resistive Zero
The inductance and capacitance of a $400$ kV, three-phase, $50$ Hz lossless transmission line are $1.6$ mH/km/phase and $10$ nF/km/phase respectively. The sending end vol...
makhdoom ghaya
9.4k
points
makhdoom ghaya
asked
Jan 29, 2017
Power Systems
gate2016-ee-2
surge-impedence
steady-state-operation
equivalent-circuit
stability-limits
+
–
0
votes
0
answers
63
GATE Electrical 2016 Set 2 | Question: 40
At no load condition, a $3$-phase, $50$ Hz, lossless power transmission line has sending-end and receiving-end voltages of $400$ kV and $420$ kV respectively. Assuming the velocity of traveling wave to be the velocity of light, the length of the line, in km, is ____________.
At no load condition, a $3$-phase, $50$ Hz, lossless power transmission line has sending-end and receiving-end voltages of $400$ kV and $420$ kV respectively. Assuming th...
makhdoom ghaya
9.4k
points
makhdoom ghaya
asked
Jan 29, 2017
Power Systems
gate2016-ee-2
lossless-power-transmission-line
traveling-wave
numerical-answers
+
–
0
votes
0
answers
64
GATE Electrical 2016 Set 2 | Question: 12
The voltage $(V)$ and current $(A)$ across a load are as follows. $v(t)=100\sin$ (ωt), $i(t)=10\sin(ωt-60°) + 2\sin(3ωt)+5\sin(5ωt)$ The average power consumed by the load, in $W$, is _________.
The voltage $(V)$ and current $(A)$ across a load are as follows.$v(t)=100\sin$ (ωt),$i(t)=10\sin(ωt-60°) + 2\sin(3ωt)+5\sin(5ωt)$The average power consumed by the l...
makhdoom ghaya
9.4k
points
makhdoom ghaya
asked
Jan 29, 2017
Power Systems
gate2016-ee-2
instantaneous-voltage-source
instantaneous-current-source
instantaneous-power
numerical-answers
+
–
0
votes
0
answers
65
GATE Electrical 2016 Set 1 | Question: 51
A single-phase transmission line has two conductors each of $10$ mm radius. These are fixed at a center-to-center distance of $1$ m in a horizontal plane. This is now converted to a three-phase transmission line by introducing a third ... more than that of the inductance per conductor of the single-phase system. The distance $D$, in meters, is _________.
A single-phase transmission line has two conductors each of $10$ mm radius. These are fixed at a center-to-center distance of $1$ m in a horizontal plane. This is now con...
makhdoom ghaya
9.4k
points
makhdoom ghaya
asked
Jan 29, 2017
Power Systems
gate2016-ee-1
transmission-system-design
transmission-parameters
transposition
numerical-answers
+
–
0
votes
0
answers
66
GATE Electrical 2016 Set 2 | Question: 54
An energy meter, having meter constant of $1200$ revolutions/kWh, makes $20$ revolutions in $30$ seconds for a constant load. The load, in $kW$, is __________.
An energy meter, having meter constant of $1200$ revolutions/kWh, makes $20$ revolutions in $30$ seconds for a constant load. The load, in $kW$, is __________.
makhdoom ghaya
9.4k
points
makhdoom ghaya
asked
Jan 29, 2017
Power Systems
gate2016-ee-2
energy-meter
revolutions
constant-load
numerical-answers
+
–
0
votes
0
answers
67
GATE Electrical 2016 Set 2 | Question: 14
A power system has $100$ buses including $10$ generator buses. For the load flow analysis using Newton-Raphson method in polar coordinates, the size of the Jacobian is $189 \times 189$ $100 \times 100$ $90 \times 90$ $180 \times 180$
A power system has $100$ buses including $10$ generator buses. For the load flow analysis using Newton-Raphson method in polar coordinates, the size of the Jacobian is$18...
makhdoom ghaya
9.4k
points
makhdoom ghaya
asked
Jan 29, 2017
Power Systems
gate2016-ee-2
taylor's-theorem
bus-admittance-matrix
pq-buses
pv-buses
acceleration-factor
+
–
0
votes
0
answers
68
GATE Electrical 2016 Set 1 | Question: 41
A $30 MVA$, $3$-phase, $50 Hz$, $13.8 kV$, star-connected synchronous generator has positive, negative and zero sequence reactances, $15\%$, $15\%$ and $5\%$ respectively. A reactance $(X_{n})$ is connected between the neutral of the ... The value of $X_{n}$ (in p.u.) that will limit the positive sequence generator current to $4270 \: A$ is ________.
A $30 MVA$, $3$-phase, $50 Hz$, $13.8 kV$, star-connected synchronous generator has positive, negative and zero sequence reactances, $15\%$, $15\%$ and $5\%$ respectively...
makhdoom ghaya
9.4k
points
makhdoom ghaya
asked
Jan 29, 2017
Power Systems
gate2016-ee-1
slip
power-system-faults
sequence-networks
numerical-answers
+
–
0
votes
0
answers
69
GATE Electrical 2016 Set 1 | Question: 40
A three-phase cable is supplying $800 kW$ and $600 kVAr$ to an inductive load. It is intended to supply an additional resistive load of $100 kW$ through the same cable without increasing the heat dissipation in the cable, by providing a three- ... voltage is $3.3 kV$, $50 Hz$, the capacitance per phase of the bank, expressed in microfarads, is ________.
A three-phase cable is supplying $800 kW$ and $600 kVAr$ to an inductive load. It is intended to supply an additional resistive load of $100 kW$ through the same cable wi...
makhdoom ghaya
9.4k
points
makhdoom ghaya
asked
Jan 29, 2017
Power Systems
gate2016-ee-1
active-power
reactive-power
heat-losses
numerical-answers
+
–
0
votes
0
answers
70
GATE Electrical 2016 Set 1 | Question: 42
If the star side of the star-delta transformer shown in the figure is excited by a negative sequence voltage, then $V_{AB}$ leads $V_{ab}$ by $60^\circ$ $V_{AB}$ lags $V_{ab}$ by $60^\circ$ $V_{AB}$ leads $V_{ab}$ by $30^\circ$ $V_{AB}$ lags $V_{ab}$ by $30^\circ$
If the star side of the star-delta transformer shown in the figure is excited by a negative sequence voltage, then$V_{AB}$ leads $V_{ab}$ by $60^\circ$$V_{AB}$ lags $V_{a...
makhdoom ghaya
9.4k
points
makhdoom ghaya
asked
Jan 29, 2017
Power Systems
gate2016-ee-1
sequence-voltages
star-to-delta-conversion
120-phase-shift
+
–
0
votes
0
answers
71
GATE Electrical 2016 Set 2 | Question: 44
A single-phase, $2$ kVA, $100/200$ V transformer is reconnected as an auto-transformer such that its $kVA$ rating is maximum. The new rating, in $kVA$, is ______.
A single-phase, $2$ kVA, $100/200$ V transformer is reconnected as an auto-transformer such that its $kVA$ rating is maximum. The new rating, in $kVA$, is ______.
makhdoom ghaya
9.4k
points
makhdoom ghaya
asked
Jan 29, 2017
Power Systems
gate2016-ee-2
auto-transformer
rating
numerical-answers
+
–
0
votes
0
answers
72
GATE Electrical 2016 Set 1 | Question: 49
A single-phase, $22 kVA, 2200 V/ 220 V, 50 Hz$, distribution transformer is to be connected as an auto-transformer to get an output voltage of $2420 V$. Its maximum $kVA$ rating as an autotransformer is $22$ $24.2$ $242$ $2420$
A single-phase, $22 kVA, 2200 V/ 220 V, 50 Hz$, distribution transformer is to be connected as an auto-transformer to get an output voltage of $2420 V$. Its maximum $kVA$...
makhdoom ghaya
9.4k
points
makhdoom ghaya
asked
Jan 29, 2017
Power Systems
gate2016-ee-1
leakage-reactance
transformation-ratio
magnetization-branch
+
–
0
votes
0
answers
73
GATE Electrical 2016 Set 1 | Question: 19
In a $100$ bus power system, there are $10$ generators. In a particular iteration of Newton Raphson load flow technique (in polar coordinates), two of the $PV$ buses are converted to $PQ$ type. In this iteration, The ... decreases by two. The number of unknown voltage angles remains unchanged and the number of unknown voltage magnitudes decreases by two.
In a $100$ bus power system, there are $10$ generators. In a particular iteration of Newton Raphson load flow technique (in polar coordinates), two of the $PV$ buses are ...
makhdoom ghaya
9.4k
points
makhdoom ghaya
asked
Jan 29, 2017
Power Systems
gate2016-ee-1
power-system-operation
iterations
jacobi-matrix
+
–
Page: